Posted By: Bocajnala Electrician Question - 02/20/24
I have 200amp service at my house.

I want to run 100amp service to a garage out back.

It's 275 feet away. I will rent a trencher, and run it in conduit underground.

The garage is small 24x32 probably.

I want to be able to run everything in there without worrying about not having enough.

220, welder, furnace, lights, tools, I want to have plenty and not need to worry about it.

What wire do I need to get this 275 feet.

Thanks

- Jake
Posted By: Bocajnala Re: Electrician Question - 02/20/24
This is what I'm coming up with. Is this right?

[Linked Image from i.ibb.co]

- Jake
Posted By: ironbender Re: Electrician Question - 02/20/24
Think you’ll be ahead to just get your electric provider to put in another 200 A drop.
Posted By: wabigoon Re: Electrician Question - 02/21/24
There are better folks than I to answer. I'll agree with 200 amp. I don't think conduit is needed.
Originally Posted by Bocajnala
This is what I'm coming up with. Is this right?

[Linked Image from i.ibb.co]

- Jake
I wouldn’t doubt it
Posted By: Bocajnala Re: Electrician Question - 02/21/24
Originally Posted by ironbender
Think you’ll be ahead to just get your electric provider to put in another 200 A drop.

Are you referring to cost? Or reliability?

Cost will be cheaper long term to run my own line to avoid paying the monthly service fee for a second service.

If it's a reliability issue due to the length... then I'll get another service. I want it to be usable and reliable.

- Jake
Posted By: Bocajnala Re: Electrician Question - 02/21/24
Originally Posted by wabigoon
There are better folks than I to answer. I'll agree with 200 amp. I don't think conduit is needed.

Copy. I'm just gathering info. If dropping another service is the right way that's what I'll do

- Jake
You might get away with smaller than a 100 amp just for a furnace and a welder .
Posted By: scottishkat Re: Electrician Question - 02/21/24
2/0 Copper is way more than needed. Are you going to feed from a breaker in the house? 2 awg copper is probably enough 1 awg copper is plenty. Aluminum 1/0 or 2/0 is plenty. The old school taught us increase 1 size for 300 feet of wire.

If you don't have to pay for utility poles etc Ironbenders advice is solid. If you're going to trench for communications probably better off doing both.

Good luck and shoot straight y'all
Posted By: Bocajnala Re: Electrician Question - 02/21/24
Originally Posted by alwaysoutdoors
You might get away with smaller than a 100 amp just for a furnace and a welder .

I don't want to get away with anything orgo the minimum. Want to do it right. I'm early 30s and no idea what I may get into some day. Want to run this the right way the first time.

- Jake
Posted By: wabigoon Re: Electrician Question - 02/21/24
I'll vote for aluminum
Posted By: rainshot Re: Electrician Question - 02/21/24
Just get another service meter. You’ll be way ahead.
Posted By: jmp300wsm Re: Electrician Question - 02/21/24
Yep iffn I was needing 200 amps then I would add another meter box. Prolly cheaper as well?
Posted By: VaHunter Re: Electrician Question - 02/21/24
How much is the anticipated maximum load needed from the 200amp service for the house lighting, heating, cooking etc., and do you really have 100amp of spare capacity?
Posted By: ironbender Re: Electrician Question - 02/21/24
Originally Posted by Bocajnala
Originally Posted by ironbender
Think you’ll be ahead to just get your electric provider to put in another 200 A drop.

Are you referring to cost? Or reliability?

Cost will be cheaper long term to run my own line to avoid paying the monthly service fee for a second service.

If it's a reliability issue due to the length... then I'll get another service. I want it to be usable and reliable.

- Jake
To be clear, I’m not an electrician. It sounds like the garage is essentially going to be a shop. 100 amp May be sufficient. Don’t know what the voltage drop at 275 feet will be. You said you don’t know what your future needs will be. It would be hard to max out a 200 A service.

Good luck.
Posted By: Alan_C Re: Electrician Question - 02/21/24
Pros and cons. Check with your utility company on your options. The home owner is responsible past the meter. A new service usually would be maintained by the utility company to the meter. If you plan to add solar, think it through. Also separate service you would be able to write off the shop bill on your taxes. If allowed someone down the road may be able to convert to guest quarters if allowed. My 2 cents.
Posted By: Bocajnala Re: Electrician Question - 02/21/24
Originally Posted by rainshot
Just get another service meter. You’ll be way ahead.
That is sounding like the right way...
Posted By: Bocajnala Re: Electrician Question - 02/21/24
I'm leaning towards a new service.

I've got a call in to a friend of a friend electrician.... hopefully he'll guide me in the right way. I do most of my own work. But admittedly don't know squat about electricity.

- Jake
Posted By: JimInAK Re: Electrician Question - 02/21/24
Pull up an ampacity chart for the type of wire you will be using. Select wire size that matches your desired amperage. This will be a starting point.

Next use an online voltage drop calculator to determine final size based on run length. You want the voltage drop percentage to be less than 3%. At 275' you will probably need to bump up a couple gauge sizes to get below 3%.

Make sure breakers and lugs will handle the upsized wiring. Select appropriate conduit size and have "fun".
Posted By: Oldman03 Re: Electrician Question - 02/21/24
https://calculator-online.net/wire-size-calculator/
Posted By: ackleydave Re: Electrician Question - 02/21/24
I would talk to someone at your local utility or wholesale
house with some electrical engineering smarts. Give him your info about distance and amperage requirements and they should be able to give you a wire size. Nothing wrong with aluminum as long as it's sized accordingly.
Posted By: KirkJ Re: Electrician Question - 02/21/24
I did the same thing in my shop, about the same distance. #3 will work for 100A. Copper individual wires in conduit. I don’t have the charts in front of me, the NEC codebook has the appropriate charts. You may want to size up 1 or 2 sizes due to length
Posted By: okie Re: Electrician Question - 02/21/24
My shop is roughly the same difference from the house BUT is down by the road where the service line is at. Full ampacity available with a separate meter and able to add anything (within reason) is nice. Cry once.....
Posted By: Rock Chuck Re: Electrician Question - 02/21/24
You have 200A in the house but will pulling from that cause a problem in the house? Electric furnace? A/C? All electric? Our house is all electric with 200A. I pulled 100A to a garage I built, then another 100 to a shop for my wife. She does art glass and runs 3 kilns, all at the same time on occasion. In the garage, I do some welding. Of course, not nearly everything runs at the same time. That's the big issue - what might the total load be at any 1 time? While you're welding, will you have clothes in the dryer and a roast in the oven? We've never had a problem yet.
Posted By: sparkman10mm Re: Electrician Question - 02/21/24
2/0 Aluminum URD

Check w/Utility for construction cost of new Service & go from there

Another consideration...Generator (either existing or future)
IF you need/ want backup power to shop bdg.
Posted By: Sheister Re: Electrician Question - 02/21/24
When I would install power to a customer's shop or other location, I would consider the load calculation before anything else is done- just like designing the service for the home to begin with.

As long as you aren't maxing out your existing 200 Amp panel at the moment (or using more than 50% at any one time) , you can run a 100 amp feeder to the shop without consequence. But the fact is, 90% of people will never use more than 50 Amps @ 240V in their shop at any one time even using a heavy use tool like a welder. You're only going to be able to use one or two tools at any one time, along with lights and possible a small heat source, so your load will be minimal at any one time.

To your question- 100 amp feed can easily be fed by #3 THHN/THWN . Voltage drop calculations include load estimates along with distance and the fact is you will seldom pull enough load for load drop to be a factor. If you would feel more comfortable #2 would be more than sufficient. For conduit for these conductors a 1" will handle 3- #3 conductors. Might want to jump up to 1 1/4" PVC for #2. Be sure to have a ground rod at the shop building and isolate the neutral conductor from the grounding/bonding bar at the panel as this will be a subpanel. It is also legal to pull a separate ground conductor with the feeders but I have found this to not be effective in breaker function at these distances.

Aluminum would also be fine as a feeder, but you would need to bump up the conduit size to accommodate the larger sized conductors. The cost difference will basically offset the difference in wire cost in the end.
Posted By: mark shubert Re: Electrician Question - 02/21/24
Originally Posted by Sheister
When I would install power to a customer's shop or other location, I would consider the load calculation before anything else is done- just like designing the service for the home to begin with.

As long as you aren't maxing out your existing 200 Amp panel at the moment (or using more than 50% at any one time) , you can run a 100 amp feeder to the shop without consequence. But the fact is, 90% of people will never use more than 50 Amps @ 240V in their shop at any one time even using a heavy use tool like a welder. You're only going to be able to use one or two tools at any one time, along with lights and possible a small heat source, so your load will be minimal at any one time.

To your question- 100 amp feed can easily be fed by #3 THHN/THWN . Voltage drop calculations include load estimates along with distance and the fact is you will seldom pull enough load for load drop to be a factor. If you would feel more comfortable #2 would be more than sufficient. For conduit for these conductors a 1" will handle 3- #3 conductors. Might want to jump up to 1 1/4" PVC for #2. Be sure to have a ground rod at the shop building and isolate the neutral conductor from the grounding/bonding bar at the panel as this will be a subpanel. It is also legal to pull a separate ground conductor with the feeders but I have found this to not be effective in breaker function at these distances.

Aluminum would also be fine as a feeder, but you would need to bump up the conduit size to accommodate the larger sized conductors. The cost difference will basically offset the difference in wire cost in the end.

^^^This^^^
When I was an electrician, many folks had no idea of "non-concurrent loads" and overbuilt as a result.
For that length of run, however, I would go one size conduit larger - for ease of pull.
Not sure, anymore, though - I've been out of the loop for 30 years (damn - that's 10 code changes!)
Posted By: GeorgiaBoy Re: Electrician Question - 02/21/24
There are several ways to approach this. So...I'll comment on the specific parameters you provided.

a. You have a 200 amp service at your house

b. You want to feed a 100 amp service at your garage

c. Your garage is 275 feet away


As others have stated - voltage drop is a determining factor. However, under your paramaters - you will be running a "feeder circuit" to your garage - not a branch circuit. Your allowable voltage drop is 2% NOT 3% as someone has stated.

The NEC puts it this way: Voltage drop on a branch circuit is 3% with a voltage drop of 5% overall.

A branch circuit is defined as the conductors "from the last overcurrent device to the load." Each circuit "inside" your garage is a branch circuit. The circuit running from your house to the garage is a "feeder circuit."

5% overall voltge drop: 3% for the branch + 2% for the feeder = 5%

If you are running a 240V Feeder to your garage, 2% voltage drop is...4.8V

Here is a simplified equation for figuring voltage dorp: I x R x L

Where: I = Current R = Resistance L = Feet of Wire Note: A circuit has two conductors - if the load is 275 feet away - you will use 550 Feet of Wire

The Details

I would not use conduit. A 275 Foot pull is VERY difficult.

I would use "triplex" direct burrial cable - and I would opt for Aluminum

Your trench must be a min of 2 feet to the top of the cable...so be safe...trench 30 inches deep.

You must protect direct burial cable to a min distance of 18" below the ground at each end where the cable emerges from the trench. No need to protect direct burial cable in-between.


Caculation

Note: The Min Size Alu Conductor For 100 amps is: #1 However, because of voltage drop, your actual wire will be larger.

#1 100 x 0.000829 x 550 = 45.6 Volts Dropped - Can't use #1

2/0 100 x 0.000523 x 550 = 28.8 Volts Dropped - Can't use 2/0

250 kcmil 100 x 0.0002778 x 550 = 15.3 Volts Dropped - Can't use 250 kcmil

500 kcmil 100 x 0.0001391 x 550 = 7.69 Volts Dropped - Can't use 500 kcmil

What's the point?

Under the parameters you stated - You Cannot Size Your Wire Large Enough To Satisify a 2% (4.8 V) Voltage Drop


I would get with your utility company. Explain what you want to do. And let them provide you with options.

Looking from where I sit - a separate service at your garage is the only real option.

A licensed Electrican from your local area may have different/better advice for you.

Respectifully,
GB
Posted By: Hutch Re: Electrician Question - 02/21/24
Don’t forget to add the length of service from transformer to house into the equation. If existing service to house is pretty long adding another 275 feet might cause too much voltage drop.
Posted By: NoDak Re: Electrician Question - 02/21/24
Originally Posted by GeorgiaBoy
There are several ways to approach this. So...I'll comment on the specific parameters you provided.

a. You have a 200 amp service at your house

b. You want to feed a 100 amp service at your garage

c. Your garage is 275 feet away


As others have stated - voltage drop is a determining factor. However, under your paramaters - you will be running a "feeder circuit" to your garage - not a branch circuit. Your allowable voltage drop is 2% NOT 3% as someone has stated.

The NEC puts it this way: Voltage drop on a branch circuit is 3% with a voltage drop of 5% overall.

A branch circuit is defined as the conductors "from the last overcurrent device to the load." Each circuit "inside" your garage is a branch circuit. The circuit running from your house to the garage is a "feeder circuit."

5% overall voltge drop: 3% for the branch + 2% for the feeder = 5%

If you are running a 240V Feeder to your garage, 2% voltage drop is...4.8V

Here is a simplified equation for figuring voltage dorp: I x R x L

Where: I = Current R = Resistance L = Feet of Wire Note: A circuit has two conductors - if the load is 275 feet away - you will use 550 Feet of Wire

The Details

I would not use conduit. A 275 Foot pull is VERY difficult.

I would use "triplex" direct burrial cable - and I would opt for Aluminum

Your trench must be a min of 2 feet to the top of the cable...so be safe...trench 30 inches deep.

You must protect direct burial cable to a min distance of 18" below the ground at each end where the cable emerges from the trench. No need to protect direct burial cable in-between.


Caculation

Note: The Min Size Alu Conductor For 100 amps is: #1 However, because of voltage drop, your actual wire will be larger.

#1 100 x 0.000829 x 550 = 45.6 Volts Dropped - Can't use #1

2/0 100 x 0.000523 x 550 = 28.8 Volts Dropped - Can't use 2/0

250 kcmil 100 x 0.0002778 x 550 = 15.3 Volts Dropped - Can't use 250 kcmil

500 kcmil 100 x 0.0001391 x 550 = 7.69 Volts Dropped - Can't use 500 kcmil

What's the point?

Under the parameters you stated - You Cannot Size Your Wire Large Enough To Satisify a 2% (4.8 V) Voltage Drop


I would get with your utility company. Explain what you want to do. And let them provide you with options.

Looking from where I sit - a separate service at your garage is the only real option.

A licensed Electrican from your local area may have different/better advice for you.

Respectifully,
GB


THIS ^^^^

You have to meet code minimum. Remember if there ever would be a fire do to wiring issues and you not doing it right can mean a denial of claim by insurance company. May cost more $ upfront but doing it right never hurts. This is no place to look cheap.
Posted By: Sheister Re: Electrician Question - 02/21/24
These posts are exactly why you need to understand voltage drop and load calculations. Using the feeder breaker size for your voltage drop calculation is not necessary nor accurate. A load calculation of what loads you would be using at any time would probably come up with about 30 Amps, including lights and using your largest tool at any one time- the welder. Once you have these parameters it makes a lot more sense to use wire suited for the calculated load and voltage drop. As a matter or course, as I said before 99% of guys who have a shop could easily get by with a 50-60 amp feeder to the shop panel and never have a problem. About the biggest load most shops have at any time is a welder or air compressor and they seldom pull more than 30 amps on the feed unless you are running a very large professional machine. Using these parameters you could easily install a 60 Amp feeder and pull the appropriate feeder for the load and distance.

How you feed underground is up to you- direct burial cable or PVC conduit is all a matter of preference. Follow code requirements for depth of burial, which is usually 24" under a non drivable surface- 36" under a drivable surface like a gravel driveway . 275 feet is a pretty good pull for most guys, but upsize one conduit size and it should be doable with a bit of help. Vacuuming in the pull line will probably be harder than the pull itself.

About the best suggestion so far is to get a local electrician to come out and tell you what you need and follow his advice. Even if you pay him a few bucks for an hour or two of his time it will be money well spent.
Posted By: GeorgiaBoy Re: Electrician Question - 02/22/24
If one is going to guesstimate how much load they are going to use at one time - it is important that the feeder overcurrent protective device be sized accordingly.

So, if one estimates their load will be no more that 50A and one sizes the wire for 50A - then one must install a breaker rated 50A.

The Feeder OCPD limits the load.

A conductor sized for 50A must not be connected to a breaker rated 100A (in general). The breaker will pass 100A. It cares not wither or not the conductors are rated for.
Posted By: Bocajnala Re: Electrician Question - 02/22/24
Several guys providing very good information

Thank you
Posted By: mark shubert Re: Electrician Question - 02/22/24
I didn't consider direct-burial cable, in spite of having installed miles of it. After I moved back into this area, I used conduit exclusively, due to pocket gophers digging into, and chewing into underground cables - I simply won't do it. Your situation very likely is much different.
Posted By: AZmark Re: Electrician Question - 02/22/24
If you go with the 2/0 copper thhn check out this price compared to what you listed, its where I buy most of my wire for my business.

https://www.wireandcableyourway.com/search/?q=2%2F0+stranded+thhn





The voltage drop calculator does show the 2/0 as needed for the voltage drop. You also can consider direct burial URD aluminum
Originally Posted by ironbender
Think you’ll be ahead to just get your electric provider to put in another 200 A drop.

I can't speak for the OP, but provided I purchased and installed the pole and box, PG&E only wanted $17K for a 100A ag panel install. My pole to be no more than 85' from the pole where they'd hang the transformer.


$17k buys one heck of a lot of gasoline for my 240v inverter...
Posted By: Fishnnut1 Re: Electrician Question - 02/22/24
I’m an electrician. Sheister is correct. Voltage drop is your enemy here more than load. Definitely get with your local power company to have a separate service installed. Preferably with a transformer near the garage.
Underground mine electrician here, if you’re anticipating needing 100 amp load being fed from your homes existing service you should have another drop installed with its own meter. That 100 amps being pulled thru your homes breaker box could cause problems in the home.
Posted By: killerv Re: Electrician Question - 02/22/24
Originally Posted by wabigoon
I'll vote for aluminum

That's what I ran out to my shop, typical trailer run stuff.

As far as conduit, depends on code I guess, I believe ours is 18in deep you have to run conduit, 24in or more you don't, something like that.

I had to get creative to add that 100amp breaker to my box inside the house, took some moving around. I'd imagine most 200amp boxes in older houses are pretty much full. I was never drawing more than 35 amps at a time out in the shop. Being the length and the tools he wants to run, I'd definitely entertain the new service idea. You don't want to worry about what you are running the house and out in the shop at the same time.
Posted By: RL Re: Electrician Question - 02/22/24
I agree with GeorgiaBoy except that I would run the triplex URD in conduit - 1/0 AL should be enough. True, the URD is made for direct bury but could be a nightmare for maintenance if you plan to have it over the long term. URD direct buried will fail - maybe not for many years or maybe in a few years - depending if you "knick" the insulation at installation, soil type, rocks, etc. Conduit is little more expense and a little more forgiving.

FYI - I have a ranch camp that is 620' from the transformer. The underground cable is direct buried 1/0 alum. My voltage fluctuates between 119/238 and 121/241 under load. It serves a 220 AC window unit, freezer, refrigerator, elect 40 gal hot water heater, and of course inside and outside lights. I did get the power company to change the bandwidth on a set of distribution regulators to where the secondary voltage at the transformer averages 126/252. That is at the high end of their tariff requirements.

Not suggesting someone do what I had to do but just saying 275' is very doable with out building a substation. You can do it with no problem without adding another meter.
Posted By: Greyghost Re: Electrician Question - 02/22/24
If you're looking to pull up to a continuous 100 amps of 240 volt into a sub-panel 275 feet away, 1/0 AWG copper cable, with a proper local ground. If you are going to be driving over the run and aren't placing it under a concrete driveway or walkway, use 1-1/2" to 2" conduit buried 18" to 24" deep. And whether or not you use conduit or direct buried cable, be damned sure back fill is free of any rocks. Personally, with the cost of electricity anymore, if this isn't going to be a 24/7 need, I'd be thinking about Solar with battery storage, or a good size generator installed at the shop.

Phil
Posted By: Bocajnala Re: Electrician Question - 02/23/24
Decided to have another service.

Thanks for the helpful advice all.
Posted By: gunzo Re: Electrician Question - 02/23/24
Originally Posted by wabigoon
There are better folks than I to answer. I'll agree with 200 amp. I don't think conduit is needed.
Originally Posted by wabigoon
I'll vote for aluminum

Are you trying to start trouble? If not,,,, just stop, please stop. And if you come up with an electrical wire term like, Water Pump Wire again, I'm gonna reach through the screen & stick a wet finger in your ear. Or you'll hope it was a wet finger. grin
Posted By: 450BM Re: Electrician Question - 02/23/24
You could put another set of lugs in your meter base and feed another 200amp panel in your garage from the same meter. This is what I did at my first house and it worked perfectly, like it should.

I would not have the power company do it and install another meter base and then pay for another service the rest of your life. I worked for an electric utility for 30 years, they own up to the meter, after that you own it and do what you want.