24hourcampfire.com
24hourcampfire.com
-->
Previous Thread
Next Thread
Print Thread
Hop To
Joined: Jun 2001
Posts: 32,080
L
las Offline OP
Campfire 'Bwana
OP Offline
Campfire 'Bwana
L
Joined: Jun 2001
Posts: 32,080
When my garage(32X40 with 16 foot walls) was framed in the contractor reinforced the doors end with plywood over the insulation, but did not put in a vapor barrier. I'm in the process or insulating, etc. the rest of it, in preparation to get the slab-heat hooked up and running.

On the door end, should I:
A) vapor barrier over the plywood before dry-walling over it
B) waterproof-tape the seams of the plywood then drywall
C) forget it and drywall
D) drywall and seal the drywall with a vapor barrier paint. And yes- no overlapping seams.


The only true cost of having a dog is its death.

GB1

Joined: Dec 2007
Posts: 17,048
Campfire Ranger
Offline
Campfire Ranger
Joined: Dec 2007
Posts: 17,048
C



BAN THE RAINBOW FLAG!
PERVERTS OFFEND ME!

"When is penguin season, daddy? I wanna go kill a penguin!"
---- 4 yr old Archerhuntress

Joined: Aug 2015
Posts: 13,234
Campfire Outfitter
Offline
Campfire Outfitter
Joined: Aug 2015
Posts: 13,234
D.
You don't want the water vapor condensing on a vapor barrier within the wall. In a cold climate the vapor will be driven from warm to cold. There is no water vapor in frozen air.
Use a heat source that doesn't add additional moisture to the inside air.


Let's Go Brandon! FJB
Joined: Jan 2001
Posts: 14,299
G
Campfire Outfitter
Offline
Campfire Outfitter
G
Joined: Jan 2001
Posts: 14,299
You've got vapor barrier on the outside why would you want it on the inside also?

Phil

Joined: Aug 2015
Posts: 13,234
Campfire Outfitter
Offline
Campfire Outfitter
Joined: Aug 2015
Posts: 13,234
Where you put the vapor barrier is dependent on your climate. Hot/tropical would be on the outside. Cold/dry would be on the inside.
The Tyvek, which is widely used for wrapping the outside of buildings is not a vapor barrier, It is a moisture barrier. Water vapor moves through Tyvek, water doesn't.


Let's Go Brandon! FJB
IC B2

Joined: Nov 2011
Posts: 330
M
Campfire Member
Offline
Campfire Member
M
Joined: Nov 2011
Posts: 330
How about we look at the Code? 2012 IRC Section R702.7 requires vapor retarders on the interior side of framed walls in specific Climate Zones. Class II vapor retarders include Kraft-faced Fiberglas batts. Class III includes latex or enamel paints that are only permitted in certain vented cladding or insulated sheathing systems.

Did your contractor perchance install Kraft-faced batts?

Bottom line is that one doesn't want warm moist interior air from occupied spaces to migrate through the wall assemblies and condense on cold exterior surfaces. If your structure has a slab-on-grade floor and the design professional/contractor didn't do a good job on the slab vapor barrier, you can get a surprising amount of water vapor migrating though the slab and into the tempered interior space as well....

Joined: Jan 2001
Posts: 21,317
Campfire Ranger
Offline
Campfire Ranger
Joined: Jan 2001
Posts: 21,317
As mentioned, you absolutely want vapor barrier between the sheetrock and the insulation.

Joined: Dec 2010
Posts: 14,408
R
Campfire Outfitter
Offline
Campfire Outfitter
R
Joined: Dec 2010
Posts: 14,408
in AK it would seem that in your case the moisture would be coming from your slab heating and you want to prevent that from going through your inside walls and hitting the cold outside wall and condensating on the inside of the sheeting. therefore i would vote for D on your finished walls and to put battened insulation facing IN on all the unfinished walls and drywalling over that. I.E, barrier facing the heat source as close as possible. i have ripped out a lot of interior walls of houses that were insulated like that and never found any signs of moisture in the walls.

Joined: Jun 2001
Posts: 32,080
L
las Offline OP
Campfire 'Bwana
OP Offline
Campfire 'Bwana
L
Joined: Jun 2001
Posts: 32,080
I was deficient in providing information.

The in-slab (to-be) heated floor is laid on several inches of rigid closed cell foam, and I believe a 10 mil (maybe only 6) sheet-plastic vapor barrier under that, so ground moisture migration should be minimal.

It was laid 5 years ago, the door end of the building in question was insulated with unfaced R-21 batts at that time, overlaid with the plywood as stated. This is the only concern I have, as to where to place a vapor barrier. It WILL get a vapor barrier, on reflection - I was posting previously at the end of an 18 hour day- not quite all there, as it were. Or as much as I am ever all there.... smile

It has been stud-wall only since, wrapped with tyvex under T- plywood siding, so moisture accumulation wouldn't have been a problem such with free passage.

I am now in the process (hopefully finishing today!) of insulating the other 3 sides of the building with un-faced R21 batts between the 2X6, 24" OC studs, and lesser OCs in some places. This will get a vapor-barrier of 6 mil sheet plastic between insulation and the sheet rock. (I was going to put plywood backing under the drywall, but I'm already over budget! The reserve is past history!)

The into- hillside, 8' concrete retaining wall opposite the doors-end was moisture sealed by the concrete contractor, and outside faced with 2 inch closed cell styrofoam, which I again covered with sheet plastic. Just for luck, I installed a French drain at footing level before back-filling that end with good sand/gravel pit run. That took me a couple weeks last summer, what with water/mechanical compacting every foot or so, and building concrete stack-walls off the end of the retaining wall, back into the hillside both sides at the same time. It ain't gong nowhere, and again ground moisture infiltration should be taken care of. Even (IF) the planned, heated floor greenhouse eventually gets put in on that end of the building (lawn level outside, with entry door into into same-level loft area of the garage).

The interior of the concrete retaining wall I furred in with 2X4, 2' OC or less and will get 3 1/2 inch unfaced batt insulation/ 6 mill sheet plastic vapor barrier as well. Above that on the frame only part, will go the R21 batts with sheet plastic VB as on the side-walls.

OK - back to the door end. Question is, will sheet plastic vapor barrier between the plywood and the sheet- rock cause rot problems in the plywood or studs? I shouldn't think so, and would be my preferred solution, but I can live with the VB paint over the drywall if necessary. Or maybe both?

This, by the way, is not in Arctic Kotzebue, but on permafrost-free/ milder climate Kenai Peninsula.


The only true cost of having a dog is its death.

Joined: Feb 2009
Posts: 6,308
D
Campfire Tracker
Offline
Campfire Tracker
D
Joined: Feb 2009
Posts: 6,308
DO NOT double vapor barrier! If it were mine, and I've done a lot of these (In lower 48), I would want the vapor barrier to the inside of the insulation. I would pull down the plywood, put up the vapor barrier sealing any penetrations or holes in the barrier with Tyvec Tape. Then put up the plywood and drywall. No VB paint.


Buy once, cry once.
IC B3

Joined: Apr 2007
Posts: 32,312
Campfire 'Bwana
Offline
Campfire 'Bwana
Joined: Apr 2007
Posts: 32,312
Kraft. It's not just for sandwiches..... smile


The CENTER will hold.

Reality, Patriotism,Trump: you can only pick two

FÜCK PUTIN!
Joined: Aug 2015
Posts: 13,234
Campfire Outfitter
Offline
Campfire Outfitter
Joined: Aug 2015
Posts: 13,234
Originally Posted by deerhunter5555
DO NOT double vapor barrier! If it were mine, and I've done a lot of these (In lower 48), I would want the vapor barrier to the inside of the insulation. I would pull down the plywood, put up the vapor barrier sealing any penetrations or holes in the barrier with Tyvec Tape. Then put up the plywood and drywall. No VB paint.


Why would you want both the plywood and the drywall on the wet side of the barrier? Great conditions to grow mold.
Why would you use Tyvek tape, which is not a vapor block, on a vapor barrier? Tyvek is specifically designed to allow moisture vapor to pass through.


Let's Go Brandon! FJB
Joined: Jan 2013
Posts: 8,248
673 Online Content
Campfire Outfitter
Online Content
Campfire Outfitter
Joined: Jan 2013
Posts: 8,248
You didn't mention...E

Is removing the plywood and installing a proper vapour barrier not an option? If it took all day to remove and install, its worth it.

Joined: Jun 2001
Posts: 32,080
L
las Offline OP
Campfire 'Bwana
OP Offline
Campfire 'Bwana
L
Joined: Jun 2001
Posts: 32,080
Originally Posted by deerhunter5555
DO NOT double vapor barrier! If it were mine, and I've done a lot of these (In lower 48), I would want the vapor barrier to the inside of the insulation. I would pull down the plywood, put up the vapor barrier sealing any penetrations or holes in the barrier with Tyvec Tape. Then put up the plywood and drywall. No VB paint.


Yeah, I thought of that. Lot of work! And probably wasted plywood that would need replacing. If contractors would use screws instead of nail guns with galvanized nails (or do it right to start with) it would make life a lot easier.

The vapor barrier will of course go on the inside.

I'm just wondering with the plywood between it and the insulation, if the plywood would soak up water from the outside ambient air and eventually rot. I don't see why it would, anymore than the studs do. I'd prefer the plywood to be inside the vapor barrier also, but that probably isn't going to happen unless I get adamant negative responses, not just from 24hr, but several local building sources.

I have a few days to think about it. The salmon are calling my name ("dip", "dip" - I'm assuming they are talking about the net.... smile ). Likely go get 10 or 12 on tomorrow morning's tide (the week-enders will be gone, and the after-worker folks not arrived), then process both the fresh and the 20 lbs or so left from last year (will brine, smoke, and can those)


Last edited by las; 06/26/16.

The only true cost of having a dog is its death.

Joined: Feb 2009
Posts: 6,308
D
Campfire Tracker
Offline
Campfire Tracker
D
Joined: Feb 2009
Posts: 6,308
Think of it like this....."conditioned" and "un-conditioned". In a perfect world, your insulation separates the two. Limiting condensation caused by sweating. The vapor barrier always goes on the conditioned side of the insulation. Think about "craft-faced" Owens Corning fiberglass insulation. The paper or "Craft-face" goes toward the room.
Any punctures or holes in the VB is a potential for moisture problems. I was taught to be anal when sealing any and all holes/penetrations in the VB. I mentioned Tyvek tape because it's common. There's a bunch more. The tape is plastic, water can't penetrate. Hope I helped.


Buy once, cry once.
Joined: Jan 2013
Posts: 8,248
673 Online Content
Campfire Outfitter
Online Content
Campfire Outfitter
Joined: Jan 2013
Posts: 8,248
las
If its that big of deal then use your 6mil poly on the plywood

tuck tape all joints and be certain there aren't any holes

make sure you acoustical seal the bottom edge of the poly

seal all edges if you have to, then drywall, it will be fine.

Joined: Dec 2003
Posts: 86,180
Campfire Oracle
Offline
Campfire Oracle
Joined: Dec 2003
Posts: 86,180
Being it's your shop and not living space, there should be far less vapor produced inside the shop than a home. I'd be more concerned with ventilation for grinding dust, welding fumes, etc.

VB with poly (sealing holes, seams, and edges) and go on with life.


If you take the time it takes, it takes less time.
--Pat Parelli

American by birth; Alaskan by choice.
--ironbender
Joined: Jul 2006
Posts: 2,095
Campfire Regular
Offline
Campfire Regular
Joined: Jul 2006
Posts: 2,095
Originally Posted by 673
las
If its that big of deal then use your 6mil poly on the plywood

tuck tape all joints and be certain there aren't any holes

make sure you acoustical seal the bottom edge of the poly

seal all edges if you have to, then drywall, it will be fine.


Help a slow learner who is lurking his way through this thread for future use on my own barn:

What is "tuck tape"? (or tuck taping, I don't know if it's a material or a method.)

What is "acoustical seal"?

TIA !!


National Rifle Association - Patron Member
National Muzzleloading Rifle Association - Life Member and 1 of 1000
Illinois State Rifle Association - Life Member
Carlinville Rifle & Pistol Club
~ Molɔ̀ːn Labé ~
Joined: Jan 2013
Posts: 8,248
673 Online Content
Campfire Outfitter
Online Content
Campfire Outfitter
Joined: Jan 2013
Posts: 8,248
Originally Posted by GunReader
Originally Posted by 673
las
If its that big of deal then use your 6mil poly on the plywood

tuck tape all joints and be certain there aren't any holes

make sure you acoustical seal the bottom edge of the poly

seal all edges if you have to, then drywall, it will be fine.


Help a slow learner who is lurking his way through this thread for future use on my own barn:

What is "tuck tape"? (or tuck taping, I don't know if it's a material or a method.)

What is "acoustical seal"?

TIA !!


Tuck tape....its red and is commonly used by insulators, it sticks like a bugger works good.

Acoustical seal.... is similiar to silicone, comes in a tube and needs a caulking gun, it never seems to dry hard and is a real pita if you get it on you, its great if it gos where you want it to and it will provide an exellent seal, which is what you want.

Joined: Jun 2001
Posts: 32,080
L
las Offline OP
Campfire 'Bwana
OP Offline
Campfire 'Bwana
L
Joined: Jun 2001
Posts: 32,080
Finally some answers I like! Affirmation, anyway, of what I wanted to do.

I'm better now...... smile

Only 3 fish in 3 hours today. Forgot the commercials were raping the resource today.

And the waders have a leak, ball-level, left side. I'm looking for it. The leak, that is, but for awhile there in that glacial water............



The only true cost of having a dog is its death.


Moderated by  RickBin 

Link Copied to Clipboard
AX24

570 members (12344mag, 1beaver_shooter, 01Foreman400, 1badf350, 10gaugemag, 1936M71, 59 invisible), 2,685 guests, and 1,312 robots.
Key: Admin, Global Mod, Mod
Forum Statistics
Forums81
Topics1,191,459
Posts18,471,154
Members73,934
Most Online11,491
Jul 7th, 2023


 


Fish & Game Departments | Solunar Tables | Mission Statement | Privacy Policy | Contact Us | DMCA
Hunting | Fishing | Camping | Backpacking | Reloading | Campfire Forums | Gear Shop
Copyright © 2000-2024 24hourcampfire.com, Inc. All Rights Reserved.



Powered by UBB.threads™ PHP Forum Software 7.7.5
(Release build 20201027)
Responsive Width:

PHP: 7.3.33 Page Time: 0.120s Queries: 14 (0.004s) Memory: 0.8904 MB (Peak: 1.0303 MB) Data Comp: Zlib Server Time: 2024-04-26 21:15:04 UTC
Valid HTML 5 and Valid CSS